5.2.1 General
The probability of structure penetration by a
lightning current is considerably decreased by
the presence of a properly designed
air-termination system.
Air-termination systems can be composed of
any combination of the following elements:
rods (including free-standing masts);
catenary wires;
meshed conductors.
To conform to this standard, all types of
air-termination systems shall be positioned in
accordance with 5.2.2, 5.2.3 and Annex A. All
types of air terminals shall comply in full with
this standard.
For all types of air terminals only the real
physical dimensions of the metal
air-termination systems shall be used for the
determination of the volume protected.
The individual air-termination rods should be
connected together at roof level to ensure
current division.
Radioactive air terminals are not allowed.
5.2.1 Загальні положення
Вірогідність проникнення струму блискавки
до будівлі (споруди) суттєво зменшується за
наявності правильно спроектованої системи
блискавкоприймачів.
Системи блискавкоприймачів можуть
складатися з будь-якої комбінації таких
елементів:
стрижні (з окремо розташованими
щоглами включно);
натягнені троси;
сітчасті провідники.
Щоб відповідати вимогам цього стандарту,
усі типи систем блискавкоприймачів мають
бути розміщені згідно з 5.2.2, 5.2.3 та
Додатком A. Усі типи блискавкоприймачів
мають повністю відповідати цьому
стандарту.
Для усіх типів блискавкоприймачів лише
реальні розміри металевих систем
перехоплення мають застосовуватися для
визначення захищеного об’єму.
Окремі стрижні блискавкоприймачів мають
бути з’єднані між собою на рівні покрівлі для
забезпечення розподілу струму.
Радіоактивні блискавкоприймачі не є
дозволеними.